Default PL8 x2 on Rsp-2000-24?

I recently got a hell of a deal on a Meanwell RSP-2000-24.

I currently run a single PL8 and would like to another one to run on this one PSU.

Am i going to run into troubles with it not being 48v? I charge 6s and 7s batteries exclusively; the majority are 5000mAH...
sl4ppy is offline        Quick reply to this message
Sponsored Links
Advertisement
 
Old 05-30-2014, 12:25 PM   #2 (permalink)
Registered Users
 

Join Date: Mar 2008
Default PL8 x2 on Rsp-2000-24?

I might be wrong, the single PL8 can take only 32V. On 27V you got the full possible current: http://www.revolectrix.com/pl8_specs_tab.htm
realloser is offline        Quick reply to this message
Old 05-30-2014, 01:08 PM   #3 (permalink)
Registered Users
 
Posts: 5,089
 
My HF Map location
Join Date: Oct 2007
Default

Quote:
Originally Posted by realloser View Post
I might be wrong, the single PL8 can take only 32V. On 27V you got the full possible current: http://www.revolectrix.com/pl8_specs_tab.htm
Correct. There are two issues to be aware of. The first is the buck boost transitions. Lowering the supply voltage about 1v would address that. Increasing it likely won't allow the transitions to clear the 7s packs.

The second issue is that if you are running from generator, as you approach the maximum output of the generator, the pulsing nature of the chargers will cause AC supply stability issues. The chargers may trigger an unstable supply safety code when you are pulling between 1300 and 1400 watts from the generator.

Be sure to set the current limit on both chargers so total current does not exceed 80 amps. Also I would run separate wires from the supply to each charger.
__________________
Revolectrix Ambassador - Charger Specialist Revolectrix.com 10% discount for Batteries GCAM16


Gregor99 is offline        Quick reply to this message
Old 05-30-2014, 01:52 PM   #4 (permalink)
Registered Users
 
Posts: 1,295
Thread Starter Thread Starter
 

Join Date: Dec 2006
Default

Quote:
Originally Posted by realloser View Post
I might be wrong, the single PL8 can take only 32V. On 27V you got the full possible current: http://www.revolectrix.com/pl8_specs_tab.htm
I guess I lucked out getting a 24v one then.

Quote:
Originally Posted by Gregor99 View Post
Correct. There are two issues to be aware of. The first is the buck boost transitions. Lowering the supply voltage about 1v would address that. Increasing it likely won't allow the transitions to clear the 7s packs.
I see in the manual that it mentions voltage trimming... Is that how you suggest I lower the supply voltage? I don't have the PSU here in front of me, but it doesn't look super obvious how that is achieved.. lol

Quote:
Originally Posted by Gregor99 View Post
The second issue is that if you are running from generator, as you approach the maximum output of the generator, the pulsing nature of the chargers will cause AC supply stability issues. The chargers may trigger an unstable supply safety code when you are pulling between 1300 and 1400 watts from the generator.

Be sure to set the current limit on both chargers so total current does not exceed 80 amps. Also I would run separate wires from the supply to each charger.
Im running a Yamaha ef2000i; it "claims" a stable output of 1600 watts.. Might that still trigger the safety code?

I assume limiting the max current to 40 amps is pretty easy to do via the standard interface.. (ie, I don't need to connect to a computer?)

(fwiw, I am currently running the single PL8 on a RSP-1000-24 which I max out pretty regularly..)

Thanks Gregor!

edit: this answered most of my questions. :0 Search rules.

https://www.helifreak.com/showthread.php?t=569144
sl4ppy is offline        Quick reply to this message
Old 05-30-2014, 04:22 PM   #5 (permalink)
Registered Users
 
Posts: 5,089
 
My HF Map location
Join Date: Oct 2007
Default

I'd first try a 6s pack at low and high currents. If you are getting the buck boost transitions lower the supply voltage. The Meanwell manual describes how this is done.

The generator is rated for constant load. The chargers put pulsing load on the supply. This makes its way up stream to the generator. The generator will attempt accommodate the pulsing load. Near the limit of the generator it becomes quite difficult for the generator and the result is an unstable AC supply.

This makes its way back down to the chargers and if its bad enough the chargers trigger an unstable supply safety code. When running two chargers, typically only one charger triggers the code aborts the charge. The load is lifted by one charger aborting and the other charger continues on.

This only happens at the upper limit of the generator. Not quite to 1600 watts. Tests were done on several Honda EU2000. Although I have not tested a Yahama, I expect to get similar results. Give it a shot and report your findings. I had posted a theory in another thread that a couple large capacitors or bank of capacitors connected to the DC side of the supply might help smooth the load on the supply and reduce the pulsing effect on the generator. I do plan on testing it, but wanted to get scope first so I can more definitely quantify the affects of different capacitors on the supply voltage.
__________________
Revolectrix Ambassador - Charger Specialist Revolectrix.com 10% discount for Batteries GCAM16


Gregor99 is offline        Quick reply to this message
Old 05-30-2014, 05:07 PM   #6 (permalink)
Registered Users
 
Posts: 2,644
 
My HF Map location
Join Date: May 2012
Location: Pacific Northwest
Default

Quote:
Originally Posted by Gregor99 View Post
a couple large capacitors or bank of capacitors connected to the DC side of the supply might help smooth the load on the supply and reduce the pulsing effect on the generator.
I love this idea!
__________________
Team MikadoUSA
hemp is offline        Quick reply to this message
 




Quick Reply
Message:
Options

Register Now

In order to be able to post messages on the HeliFreak forums, you must first register.
Please enter your desired user name, your REAL and WORKING email address and other required details in the form below.
User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself. Use a real email address or you will not be granted access to the site. Thank you.
Email Address:
Location
Where do you live? ie: Country, State, City or General Geographic Location please.
Name and Lastname
Enter name and last name here. (This information is not shown to the general public. Optional)
Helicopter #1
Enter Helicopter #1 type and equipment.
Helicopter #2
Enter Helicopter #2 type and equipment.
Helicopter #3
Enter Helicopter #3 type and equipment.
Helicopter #4
Enter Helicopter #4 type and equipment.

Log-in


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On




Copyright © Website Acquisitions Inc. All rights reserved.
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.

SEO by vBSEO 3.6.1